Author Topic: Busbar It and operating temeratures  (Read 78 times)

Offline thood.bsec

  • Newbie
  • *
  • Posts: 4
  • Karma: +0/-0
Busbar It and operating temeratures
« on: 07 June 2024, 10:50 »
I have noticed that bus bar actual operating temperatures are showing as exceeding 70 degrees when design currents are less than half the bus bar rating Iz.  The software also applies a 0.86 Ct correction factor to the bus bar for 70 degree operating.

Q1: Why would the bus bar exceed its rated operating temperature before its rated It is reached when no correction factors need be applied?
Q2. Why would the software de-rate the bus bar to operate at 70?

There is lots of information on design in the Schneider catalogue including specific de-rating factors for ambient temperature and CPD type but there is no de-rating when installed in ambient of 35 or less and protected by an MCCB (my install).



Offline admin

  • Administrator
  • Newbie
  • *****
  • Posts: 19
  • Karma: +4/-0
Re: Busbar It and operating temeratures
« Reply #1 on: 07 June 2024, 11:11 »
Hi,

The Ct factor only applies to the voltage drop calculations in Appendix 4 in BS767.

The software checks based on the limit specified by the user. In your case 70oC. Please see the image below too