Parallel conductor It(A) critical message
«
on:
08 November 2023, 09:44 »
I always get a critical message when using parallel conductors, the It(A) is only calculating the single conductor and not the parallel conductor. Is there a way to clear the critical warning.
Logged
Mert
Administrator
Newbie
Posts: 42
Karma: +5/-0
Re: Parallel conductor It(A) critical message
«
Reply #1 on:
08 November 2023, 10:38 »
EOM calculates and displays the result for one conductor of a parallel bunch, so, what you see is the current would pass through via one conductor of the whole bunch. To remove this you need to reconsider your cross-sections.
Logged
jw
Newbie
Posts: 1
Karma: +1/-0
Re: Parallel conductor It(A) critical message
«
Reply #2 on:
10 November 2023, 21:13 »
Spacing the cables, if possible, can help as the grouping factor will not be considered
Logged