Author Topic: Parallel conductor It(A) critical message  (Read 1739 times)

Offline mattwilson83

  • Newbie
  • *
  • Posts: 1
  • Karma: +0/-0
Parallel conductor It(A) critical message
« on: 08 November 2023, 09:44 »
I always get a critical message when using parallel conductors, the It(A) is only calculating the single conductor and not the parallel conductor. Is there a way to clear the critical warning.



Offline Mert

  • Administrator
  • Newbie
  • *****
  • Posts: 41
  • Karma: +5/-0
    • ElectricalOM
Re: Parallel conductor It(A) critical message
« Reply #1 on: 08 November 2023, 10:38 »
EOM calculates and displays the result for one conductor of a parallel bunch, so, what you see is the current would pass through via one conductor of the whole bunch. To remove this you need to reconsider your cross-sections.

Offline jw

  • Newbie
  • *
  • Posts: 1
  • Karma: +1/-0
Re: Parallel conductor It(A) critical message
« Reply #2 on: 10 November 2023, 21:13 »
Spacing the cables, if possible, can help as the grouping factor will not be considered