Schematic Bus-Bar
« on: 05 October 2021, 13:50 »
I'm plotting a design using the schneider KN bus-bar but can only place 1 tap off on one side of the bus-bar the type i'm installing as 6 tap offs on each length. Can this be fixed?

Offline Mert

  • Administrator
  • Newbie
  • *****
  • Posts: 41
  • Karma: +5/-0
    • ElectricalOM
Re: Schematic Bus-Bar
« Reply #1 on: 05 October 2021, 13:51 »
You can install up to two tap-offs / section. You can add extra sections and set them not to use conductors. This will allow you to add as many taps and consider only only section.

See the attached image for guidance.