Title: Parallel conductor It(A) critical message
Post by: mattwilson83 on 08 November 2023, 09:44
I always get a critical message when using parallel conductors, the It(A) is only calculating the single conductor and not the parallel conductor. Is there a way to clear the critical warning.

(https://i.postimg.cc/mPdYgWfh/OM-parallel-conductors-critical-message.png) (https://postimg.cc/mPdYgWfh)
Title: Re: Parallel conductor It(A) critical message
Post by: Mert on 08 November 2023, 10:38
EOM calculates and displays the result for one conductor of a parallel bunch, so, what you see is the current would pass through via one conductor of the whole bunch. To remove this you need to reconsider your cross-sections.
Title: Re: Parallel conductor It(A) critical message
Post by: jw on 10 November 2023, 21:13
Spacing the cables, if possible, can help as the grouping factor will not be considered
(https://i.postimg.cc/Sn55hdKB/OM-parallel-conductors-critical-message-2.png) (https://postimg.cc/Sn55hdKB)